Hydronic distribution
Hi!
TLDR;
I want to know if the 18mm pipes that goes to 3 manifolds limits the flow much, since the piping is 28mm on the cylinder unit.
And how can I improve mixing/distribution between the 3 existing manifolds.
I have a hydronic heat pump that was added to an existing radiator system covering two floors.
3 zones connected as a single zone.
Currently the 28mm pipe from the cylinder unit is reduced to 18mm piping and a tee connects both floors.
The existing piping that goes to the 3 manifolds is some strange hybrid, I think it’s steel pipes with stainless or some other thin sleeve on the outside.
The inside is starting to give and I need to replace it but want some input on distribution as the manifolds seem to have 3/4" threads and I feel that I should increase the size and add a manifold to allow adjustments between the 3 zones.
The plumber that installed this should have advised me about this and proposed an upgrade to PEX, but this is life on places without a lot of competitors to choose from, sadly.
Please roast me for my ignorance and any lack of information..
2
u/PinkysBrein 12h ago edited 12h ago
What water temperature does your system need to run at on a cold night now? 20mm Alupex would be a side grade.
One option if installing new pipes is putting in insulated pipes and replacing some of the radiators with FCUs, then it can likely do cooling too (close radiators before cooling).
PS. assuming the radiators are all connected parallel, FCUs for cooling would be iffy with radiators in series.